Coleman DGAA blower fan speed

Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
solden
Posts: 12
Joined: Wed Nov 24, 2010 12:57 am

Hi, I have a coleman- DGAA and split a/c system . just turned on heat for the season in iowa. however the blower will only run on high speed . wires are right on the thermostat & control board if i take the high speed wire off the cool terminal fan won't run , only with high speed on cool terminal , i'm guessing the relay on the board is bad ? also a little bit of a grumbling noise when fan first starts bearing dry, no play in shaft ,wheel is clean :?:
gordo48111
Posts: 67
Joined: Fri Nov 12, 2010 10:45 am

Until Robert replies to this post, does the blower run constantly or only when there is a call for heat?
"Man...that blowed up real good!"
solden
Posts: 12
Joined: Wed Nov 24, 2010 12:57 am

no it runs fine regular cycle , just on high speed
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,

Test board and see if you 24vac across W and C.

Then, see if you have 120vac across HEAT terminal and one of the NEUTRAL terminals.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
solden
Posts: 12
Joined: Wed Nov 24, 2010 12:57 am

yes i have 26 vac across w and c and 120 on heat terminal , so since the fan motor is a grumbling at start up for a few seconds could it be a bad motor ?
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

IF there is a fan run capacitor, replace it first. IF there is no change, then motor is most likely bad.

Can give order info on parts if needed.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
solden
Posts: 12
Joined: Wed Nov 24, 2010 12:57 am

hi, i see this is a 7.5 mfd 50/60 hz 440 vac , i can get one local for 8.00 but it's a 370 vac any problems with that. if so i,ll just let it run it till i can afford a new unit motor and all

thanks for all your help
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Must be 440. IF you ever have one that is 370, replacement can be 370 or 440.

For 440 though, it must be same.

Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
solden
Posts: 12
Joined: Wed Nov 24, 2010 12:57 am

OK, thanks for all your help it runs fine just on high speed cools the some temp down at the registers,
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

You're very welcome, happy to help.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
solden
Posts: 12
Joined: Wed Nov 24, 2010 12:57 am

Hi, the park manager has a run cap. that is a ngm s1-02435602000 single 7.5 440 rectangular. its made of plastic he said it would work ,is that true don't want to have a fire.
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

As long as it is 7.5mfd / 440vac .


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?