Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
Bobc

My son has an EB20B furnace in a double wide home. The air temp, from the vents, never goes over 86º. Is this normal? We can hear clicking in the furnace quite often, I assume this is the sequencer. All elements measure 12 ohms and when first turned on, there is 240 valts AC across each one. The voltage to the coils starts sequencing off fairly soon after turning on.

Thank you for your help,
Bobc
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Could be a faulty Sequencer. It controls the lements and blower motor.


Sequencer # 3120A3571 @ $50.64 + $6.00 shipping .


It can be seen and ordered from left side here through PayPal:

http://www.mobilehomerepair.com/ColemanElec.html


OR, by calling toll free between 9A/5P CST Mon thru Fri to

1-877-263-7860 and charging to Visa or Mastercard.



Thanks for inquiring,
Robert