Replacing a 7610-859 with a 7956C856. Will my old chimney / exhaust pipe work on the new heater ? The vent gas outlet size looks about 5 inches on both and the bigger fresh air inlet size looks about 8 inches on both. Planning on doing this today and hoping I can reuse the chimney / roof jack and not have to replace it.

Re: chimney size question

Posted: Wed Nov 26, 2014 7:39 pm
by Greg
If it is in good shape I don't think there should be a problem using the old on as long as it is the same size pipe.

Greg

Re: chimney size question

Posted: Wed Nov 26, 2014 10:01 pm
by digifoss
Got the heater changed out today, finally. Still on it's first cycle right now but is heating good. I re-used my old chimney. The center pipe was still round and in good shape and fit good and snug on the exhaust riser on the heater. The outer pipe was a little bent out of round - was already that way. Old heater had a piece of metal flashing wrapped around the outer pipe and taped with hi-temp aluminum tape to the top of the heater and the flashing wrap so I did the same but I took better care to make sure it was sealed good all the way around top and bottom. So far so good.