I have a Nordyne E3EB 012H system with Air.
Everything seems to be working ok, except that the elements doesn't kick in at all times, only sometimes. I have searched this forum and did test. I took out the elements and tested good.
I tested the wires coming out of the contactor and they read 120 all times, also the other red wires on the other side of the elements is reading 120. However, when the elements are NOT working there isn't 240 across. But when they do work, there is 240 across each one. I also noticed that the 120 decreases some on each terminal. I have a ohmeter and tester. Can you give me more specifics of what componets to track this problem down? Also when the elements do work there is a click from the contactor. But I'm unsure if it is the contactor bad or the limit switch or something else. The fan works good and seems like it should, just not getting heat good, and blows just fan air most of the time. Thank you in advance.
E3EB 012H Elements only working some
When it does this and you do not have 240vac across, test each end to unpainted metal ground for 120vac and see which is not getting power.
Thanks,
Robert
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 0 Replies
- 103245 Views
-
Last post by Colbey8466
Mon Feb 10, 2020 3:44 am
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 158018 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Eb15a elec furnace will only come on if jumpered at themostat
by redcat31 » Wed Jan 31, 2018 6:18 pm » in Service & Repair of Other Brands - 0 Replies
- 20991 Views
-
Last post by redcat31
Sat Feb 03, 2018 1:20 am
-
-
- 4 Replies
- 7986 Views
-
Last post by Norm Frechette
Thu Sep 07, 2017 5:27 am
-
- 1 Replies
- 35693 Views
-
Last post by Greg
Fri Apr 20, 2018 5:11 pm