Miller Furnace-no heat

Posted: Fri Oct 15, 2010 2:52 pm
by Suefie
I have a no heat situation with my Miller furnace in my 4 year old manufactured home, model #M3RL080ABW. Since replacing thermostat, furnace will not come on. The programmable thermostat has been tested and it is good and wired correctly. Even when reinstalling the manual stat, no heat. Furnaces transformer is humming. Suggestions would be greatly appreciated.

Re: Miller Furnace-no heat

Posted: Fri Oct 15, 2010 11:49 pm
by Robert
Test transformer for proper voltage. Line/Primary side = 120vac. Load/Secondary side = 24vac.

Real easy to blow a transformer when wiring a t-stat if not careful. Or could have just went bad at that time.



Thanks,
Robert