Hi Jim,
The 1 at end of p/n is an added number our distributor puts on all parts., has no meaning to part.
All top and middle terminals are M's and the very bottom are H's.
The wiring is same for both old and new.
Try the ohms test suggested to see what it shows.
Thanks,
Robert
Coleman furnace blower will not come on
Different set of contacts that are working. However, it needs to be on M1/M2 at the M2 side which is start of the elements.
Thanks,
Robert
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi Robert,
This is what you had previously wanted me to do:
Remove wires from M1 and M2 ONLY. Turn t-stat OFF.
Set meter to test for ohms and test across M1 and M2.
Then set t-stat to Heat-Auto-highest temp setting to get a call for heat.
Wait 30 seconds and test ohms across M1 and M2 again.
Tell me what it reads.
In each case, I got a zero reading. It seems that with the previous readings that the new sequencer is giving off the correct readings. Still, with the blower wire connected to M6 and operating correctly, doesn't that mean that the other half of the sequencer is not working correctly?
Either way, I feel that we have achieved some sucess and again, I do appreciate your help.
Thanks,
Jim
This is what you had previously wanted me to do:
Remove wires from M1 and M2 ONLY. Turn t-stat OFF.
Set meter to test for ohms and test across M1 and M2.
Then set t-stat to Heat-Auto-highest temp setting to get a call for heat.
Wait 30 seconds and test ohms across M1 and M2 again.
Tell me what it reads.
In each case, I got a zero reading. It seems that with the previous readings that the new sequencer is giving off the correct readings. Still, with the blower wire connected to M6 and operating correctly, doesn't that mean that the other half of the sequencer is not working correctly?
Either way, I feel that we have achieved some sucess and again, I do appreciate your help.
Thanks,
Jim
Hi Jim,
With a call for heat and after 30 seconds, you should have got a reading showing ohms and a closed circuit.
The blower wire must be on M2.
By what you stated, M1 to M2 contacts are not closing.
However, you also stated all elements have voltage and are working.
IF all elements are receiving full voltage and all are working, then the blower motor is getting voltage through the sequencer.
Therefore, need to check the molex plug connector wires as stated earlier.
Thanks,
Robert
With a call for heat and after 30 seconds, you should have got a reading showing ohms and a closed circuit.
The blower wire must be on M2.
By what you stated, M1 to M2 contacts are not closing.
However, you also stated all elements have voltage and are working.
IF all elements are receiving full voltage and all are working, then the blower motor is getting voltage through the sequencer.
Therefore, need to check the molex plug connector wires as stated earlier.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Eb15a elec furnace will only come on if jumpered at themostat
by redcat31 » Wed Jan 31, 2018 6:18 pm » in Service & Repair of Other Brands - 0 Replies
- 19811 Views
-
Last post by redcat31
Sat Feb 03, 2018 1:20 am
-
-
- 2 Replies
- 17340 Views
-
Last post by TorstenW
Tue Mar 06, 2018 1:04 am
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 153998 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 107263 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
- 2 Replies
- 22237 Views
-
Last post by plumducky
Tue Dec 10, 2019 3:59 pm