Hi Folks--- I have a Nordyne furnace that works ok (except for drawing lots of current) and a Evcon MBC48DQA Refrigeration Unit.
The outside A/C fan does not turn on at all. The A/C was unused for about 4 or 5 years until I moved it to my place and had the electricians hook it up. The fan turns freely when I spin it. The name and data plate are missing. Would any body have any ideas about Brand name or any good way to figger out repair or replacement. I have a 16X80 1997 Redman.
Thanks ,
Hose6161
Nordyne model E1EH-015HA
Did you check the power supplied to the unit? Fuses and breaker ?
If it spins freely it is more than likely a power problem. Also make sure your thermostat is set for A/C use.
Next does the compressor kick in when the fan is not running?
Is the outdoor units contactor/starter pulling in?
Check for 24 volts to the outside unit on the control circuit line at the contactor/starter.
If it spins freely it is more than likely a power problem. Also make sure your thermostat is set for A/C use.
Next does the compressor kick in when the fan is not running?
Is the outdoor units contactor/starter pulling in?
Check for 24 volts to the outside unit on the control circuit line at the contactor/starter.
God, grant me the serenity
to accept the things I cannot change;
the courage to change the things I can;
and the wisdom to know the difference.
to accept the things I cannot change;
the courage to change the things I can;
and the wisdom to know the difference.
Hi,
Since it is a Coleman/Evcon A-Coil, outside Condenser is most likely Coleman/Evcon also.
That is a 4 ton a-coil which is most likely oversized for a 16X80 home.
I'm in a 16X80 and have a 3 ton.
Your blower motor in furnace may not support a 4 ton (1600 cfm).
Check all the things HVAC suggested and let us know.
Take care and best wishes,
Robert
Since it is a Coleman/Evcon A-Coil, outside Condenser is most likely Coleman/Evcon also.
That is a 4 ton a-coil which is most likely oversized for a 16X80 home.
I'm in a 16X80 and have a 3 ton.
Your blower motor in furnace may not support a 4 ton (1600 cfm).
Check all the things HVAC suggested and let us know.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Thanks for the promp reply folks. I'll check those things when I go home in a coupla weeks( Right now i'm 440 miles from it)
Hose
Hose
Hi Hose,
You're very welcome. Let us know when you can and we'll help all we can.
Take care and best wishes,
Robert
You're very welcome. Let us know when you can and we'll help all we can.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Nordyne Mod. E1EH-015HA split unit/eliminate cooling?
by carolina jim » Thu Oct 24, 2019 8:33 am » in Nordyne Service & Repair - 0 Replies
- 39283 Views
-
Last post by carolina jim
Thu Oct 24, 2019 8:33 am
-
-
- 2 Replies
- 25607 Views
-
Last post by Maxwell.lipphardt
Mon Feb 04, 2019 6:35 am
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 167224 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Nordyne model m1mb 070a bw power issue
by Combustibleink » Mon Nov 16, 2020 10:21 am » in Nordyne Service & Repair - 0 Replies
- 115863 Views
-
Last post by Combustibleink
Mon Nov 16, 2020 10:21 am
-
-
-
Question about burned wiring on e2eb-015ha
by thomasclay » Thu Sep 14, 2017 5:37 pm » in Nordyne Service & Repair - 0 Replies
- 65252 Views
-
Last post by thomasclay
Thu Sep 14, 2017 5:37 pm
-