Intertherm Model MGHB-056ABFC-09
Posted: Fri Aug 21, 2009 9:11 am
by JohnH
There is no air coming out of floor vents when the AC is on. Motor fan is running, I have replaced limit switch and fan switch, plus thermostat.
RE: Intertherm Model MGHB-056ABFC-09
Posted: Sat Aug 22, 2009 1:39 am
by Robert
Hi,
Double or single wide ?
NO air at all out of ANY register ?
Thanks,
Robert
Re: RE: Intertherm Model MGHB-056ABFC-09
Posted: Sun Aug 23, 2009 12:30 pm
by JohnH
Robert wrote:Hi,
Double or single wide ?
NO air at all out of ANY register ?
Thanks,
Robert
It will blow cold air for a short time and then stops, but the blower is still running.
Double wide
RE: Intertherm Model MGHB-056ABFC-09
Posted: Sun Aug 23, 2009 6:47 pm
by Robert
The air keeps flowing, just not cold anymore or the air flow stops all together.
Thanks,
Robert
Re: RE: Intertherm Model MGHB-056ABFC-09
Posted: Mon Aug 24, 2009 1:57 am
by JohnH
Robert wrote:The air keeps flowing, just not cold anymore or the air flow stops all together.
Thanks,
Robert
Air flow stops all together, btw thanks for the help
RE: Intertherm Model MGHB-056ABFC-09
Posted: Mon Aug 24, 2009 10:11 am
by Robert
Hi,
When the airflow stops, does it stop completely flowing from every register in both halves of the home ?
Have you removed door panel and visually seen that blower motor was still running and blower wheel turning ?
There is a smaller motor that runs also (draft inducer motor).
IF the blower motor and wheel are turning/running full speed, but you have zero airflow from any registers, there is a blockage or a duct loose somewhere.
IF it is just on the side opposite the furnace, then most likely a crossover duct blocked, loose or torn.
Thanks,
Robert