Furnace - Central Electric - Model # EB15B
Posted: Tue Mar 10, 2009 1:40 pm
by swr470
Posted: Tue Mar 10, 2009 2:17 pm
by Mark
Hi,
Just the blower running wouldn't run up the electric bill a whole lot, so you must also have one element not turning off either. To fix this, replace the sequencer. For your furnace, that is part number 3115-3571. It can be seen and ordered on this page of our website:
http://www.mobilehomerepair.com/ColemanElec.html
Thanks,
Mark
RE: Furnace - Central Electric - Model # EB15B
Posted: Tue Mar 10, 2009 11:07 pm
by swr470
I will order the recommended part. Thanks Mark.
RE: Furnace - Central Electric - Model # EB15B
Posted: Fri Apr 24, 2009 1:55 pm
by swr470
installed the sequencer as suggested. Blower motor still runs.......any other suggestions
RE: Furnace - Central Electric - Model # EB15B
Posted: Mon May 04, 2009 4:16 pm
by Robert
The sequencer controls the blower motor for heating mode.
Will need to test circuit to motor to find where it is being energized from.
Also, doublecheck sequencer wiring and make sure motor is wired from output side of M1 and M2.
Thanks,
Robert