Goodman/Janitrol GPD100-4 Burners not firing consistently
I have a Goodman/Janitrol GPD100-4. After the heating element gets hot and the gas ignites, I get inconsistent firing across the four burners. The one on the far right with the heating element burns correctly, but the other three ignite and turn off repeatedly. This lasts for about 4-5 seconds and then the gas cuts off. This cycle will repeat for the duration of the cycle and the temperature of the house may or may not rise until the furnace cuts off. I usually have to turn the thermostat down at least one degree below the current temp and then back up at least one degree over the current temp to get it to kick on again. In addition, the strange thing is that I have witnessed all four burners burning properly for 10-15 seconds on many occasions, so the problem seems intermittent, although the on again/off again is the most common symptom. Any help would be great. Thanks!
Hi,
Check burners and burner orifices for blockages of any kind (spider/web is common).
IF all ok, best to call an hvac tech in to properly diagnose problem for safety.
Thanks,
Robert
Check burners and burner orifices for blockages of any kind (spider/web is common).
IF all ok, best to call an hvac tech in to properly diagnose problem for safety.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Thanks for your response, Robert! I took it all apart, cleaned everything including a light sanding of the flame sensor, and put it all back together. When I fired it up I got the same result, at first. After about 30 minutes of normal operation, all four burners were blazing away properly. The next day, same issue again. This is the weird thing. It works correctly sometimes and incorrectly other times. I have a feeling that it will be a classic case of a service call, that when I get someone to look at the problem, it will function as it is supposed to and go back to what it was doing as soon as they leave.
Hi Dave,
Those calls do happen and irritate the service techs also and are very hard to diagnose.
Takes some patience, isolating circuits and and one by one determine the fault.
Clean flame sensors with steel wool, but htey are usually ok besides being oxidized somewhat.
Keep us posted, maybe it will act up and an hvac tech can come quickly and see what it is.
Thanks,
Robert
Those calls do happen and irritate the service techs also and are very hard to diagnose.
Takes some patience, isolating circuits and and one by one determine the fault.
Clean flame sensors with steel wool, but htey are usually ok besides being oxidized somewhat.
Keep us posted, maybe it will act up and an hvac tech can come quickly and see what it is.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 65452 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 105415 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Heat strips are on, but not the fan.
by Forestbrook » Sat Dec 08, 2018 6:09 pm » in Coleman Service & Repair - 0 Replies
- 36939 Views
-
Last post by Forestbrook
Sat Dec 08, 2018 6:09 pm
-
-
- 2 Replies
- 21069 Views
-
Last post by plumducky
Tue Dec 10, 2019 3:59 pm
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 150946 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-