Page 1 of 1

Miller Furnance M3RL080A BW

Posted: Thu Feb 05, 2009 10:22 am
by rtl
I have the above listed furnance in my home. The problem is that the inducer fan motor limit switch keeps triping. I have had two service tecs look at the furnance and they still can't get it working right. My question is on the inducer motor does the limit switch have a manual reset button and what is the limit switch suppose to be rated at. I think mine has been changes by a serviceman and I want to make sure he put the right one back in. It has a reset button and is rated for 230 degrees.

RE: Miller Furnance M3RL080A BW

Posted: Sat Feb 07, 2009 3:13 pm
by Rod
Check the restrictor plate/orifice behind the inducer motor. Should be the size of a silver dollar with a hole in the middle the size of a quarter. (apprx) Nordyne has been having problems with these melting. If this is the case your switch will probably trip. The Nordyne part # for the switch is 626499 & the inducer orifice is 155315R. You should be able to order through this site. Hope this helps.

Rod

RE: Miller Furnance M3RL080A BW

Posted: Tue Feb 10, 2009 2:13 am
by Robert
Hi,

Yes, it has manual reset button and is rated at L145 .



Thanks,
Robert