Intertherm Model MMHB-070ABHR-06
Unit wont start after a few minutes of cycling and the Control Module Status Indicator flashes 3 times continuously.
Indicator panel says that three flashes means:
Failed ignition attempt, a gas valve error, or a false flame sensed during the warmup period
Any suggestions as to possible repair attempt?
Thank you
Intertherm gas furnace model MMHB-070ABHR-06 wont start
Hi,
Control Module: On call for heat:
L1 and L2 = 120vac
IND and L2 = 120vac
After approx. 1 minute :
HSI and HSIG = 120vac
PSI and C = 24vac
PSO and C = 24vac
GV and C = 24vac
Thanks,
Robert
Control Module: On call for heat:
L1 and L2 = 120vac
IND and L2 = 120vac
After approx. 1 minute :
HSI and HSIG = 120vac
PSI and C = 24vac
PSO and C = 24vac
GV and C = 24vac
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
3500A816 Randomly wont start or shut down
by Smithcraft » Fri Jan 13, 2023 4:04 pm » in Coleman Service & Repair - 0 Replies
- 86092 Views
-
Last post by Smithcraft
Fri Jan 13, 2023 4:04 pm
-
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 65571 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-
-
- 14 Replies
- 160348 Views
-
Last post by Greg
Tue Sep 26, 2017 1:00 pm
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 105532 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 151131 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-