Coleman Evcon Presidential pilot won't light
Posted: Tue Nov 11, 2008 5:46 pm
Heya guys you helped me out last year, hopefully I can get it running again with your help.
Model DGRT070AUA gas furnace. Has the pilot reigniter box, both T1 and T2 have power, on a call for heat T1 is at 12v T2 is between 12 and 15v. The high voltage lead does not have any current at idle, call for heat or even when attempting to light the pilot with the switch held in the "on" position on the gas control assembly.
With the sight glass removed, I was unable to light the pilot manually, and the gas control valve does not have any power coming to it from the upper limit switch. (the one with the little red button that pops up when it's over limit) and at that switch there is no power on either side.
Any help will be greatly appreciated.
Thanks,
Daniel
Model DGRT070AUA gas furnace. Has the pilot reigniter box, both T1 and T2 have power, on a call for heat T1 is at 12v T2 is between 12 and 15v. The high voltage lead does not have any current at idle, call for heat or even when attempting to light the pilot with the switch held in the "on" position on the gas control assembly.