Page 2 of 2

Posted: Fri Dec 07, 2007 5:37 pm
by GarryW
On Tuesday, I called a Coleman Service rep about 40 miles away from me. I was willing to have him come and see what he could do but after I related my tale of woe to that point he asked one simple question: "When you cleaned the orifice, did you take it completely apart?"

You can guess the rest. Cleaned out the spider and the rest of his nest, furnace works better than it has since I bought the place.

I'm happy...cat's happy...dog stopped shivering.

Thanks for everything, Robert...I did learn a lot about my furnace.

Happy Holidays...Garry W.

RE: Coleman 7900 Series Intermittent Blower

Posted: Fri Dec 07, 2007 5:56 pm
by Robert
Hi Gary,

I had that same thought, but since you said you cleaned it, I didn't go there.

In the past I usually would have, but you would not believe how many times I've been cussed out here and in private emails because I stated "do it again" or "check it again" or "are you sure,etc." .


EVERYTHING you posted pointed at the orifice and I apoligize for not jumping in head first once again.


Merry Christmas !!


Take care and best wishes,
Robert