Furnace - Central Electric - Model # EB15B

Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
swr470
Posts: 4
Joined: Tue Mar 10, 2009 1:33 pm
Location: Kentucky

The blower motor runs continuously. I have to turn it off at the breaker. The heating unit kicks on and off at the correct temperature, but the blower never stops. Please help.....this is killing my monthly electric bill :!: :!: :!:
User avatar
Mark
Site Admin
Posts: 742
Joined: Sat Feb 17, 2007 4:23 pm
Location: Aberdeen, SD
Contact:

Hi,

Just the blower running wouldn't run up the electric bill a whole lot, so you must also have one element not turning off either. To fix this, replace the sequencer. For your furnace, that is part number 3115-3571. It can be seen and ordered on this page of our website: http://www.mobilehomerepair.com/ColemanElec.html

Thanks,
Mark
You can't fail if you don't try!
swr470
Posts: 4
Joined: Tue Mar 10, 2009 1:33 pm
Location: Kentucky

I will order the recommended part. Thanks Mark.
swr470
Posts: 4
Joined: Tue Mar 10, 2009 1:33 pm
Location: Kentucky

installed the sequencer as suggested. Blower motor still runs.......any other suggestions :?:
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

The sequencer controls the blower motor for heating mode.


Will need to test circuit to motor to find where it is being energized from.


Also, doublecheck sequencer wiring and make sure motor is wired from output side of M1 and M2.



Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?