coleman 7665-856
i had a problem with the blower running for about 30 seconds then shutting down for a minute or two and then coming back on for 30 secons. i bought a new fan switch and installed it. after installation the blower would not come on. i turned power switch off and put the old one back in, then turned power back on. now the burner wont ignite (pilot light is on). there is a humming noise coming from the transformer. is the transformer bad? what else would cause the fan from coming on?
The transformer may be bad, would have to check voltages to know.
Also check burner and orifice for blockages.
Thanks,
Robert
Also check burner and orifice for blockages.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
before the burner wouldnt light it would make a click noise coming from the area of the valve a split second before the burner would light thats why i was thinking that the transformer is bad. i wish i had a way to test the voltage but i dont.
Most supply stores for electric parts, hvac, etc. will have a set up to check transformers for you.
Or, a decent meter can be found for $20 in big box stores, etc.. .
Thanks,
Robert
Or, a decent meter can be found for $20 in big box stores, etc.. .
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 0 Replies
- 13616 Views
-
Last post by Ggandme2019
Thu Oct 10, 2019 5:58 am
-
- 2 Replies
- 56492 Views
-
Last post by jazsimpson
Sat Jul 08, 2017 8:16 am
-
- 0 Replies
- 54359 Views
-
Last post by Montanan
Wed Jan 03, 2018 1:03 pm
-
- 0 Replies
- 47315 Views
-
Last post by Kourgath
Fri Mar 23, 2018 3:41 pm
-
-
LOUD Blower on Coleman Presidential 2 900759
by AuntKatie » Thu Apr 05, 2018 6:50 pm » in Coleman Service & Repair - 0 Replies
- 41766 Views
-
Last post by AuntKatie
Thu Apr 05, 2018 6:50 pm
-