Nordyne M1MB 090A Burner won't remain lit

Questions about repairs and parts for Nordyne furnaces, air conditioners and heat pumps for manufactured homes including Intertherm, Mac and Miller brands. Click here for Nordyne parts.

Moderators: Greg, Mark

Locked
jonathan teller

The main gas valve ignites fine ! but only stays on for 5 or 6 seconds then dies!!! The flame sensor does detect a flame for those 5 or 6 seconds (yellow led glows steady). I've replaced the glow plug/sensor. I've replaced the entire gas valve. Still no luck!!
By the way the furnace is 2 years old but I have personally never seen it work. Jonathan 727-5424294
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi Jonathan,

If it never has worked, did you ever call out a Tech while still under warranty ?


Place meter leads on the gas valve terminals and see if the gas valve remains energized at time it stops or does it lose the 24-28VAC.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
jonathan teller

I'll go test those terminals. Thanx for unbelievably rapid response!
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi Jonathan,

You're very welcome.



Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?