Elements continue to heat after fan kicks off. Replaced sequencer but that did not help.
THanks,
E2EB-015HA problems
Hi,
First, be sure it isn't the t-stat by removing the W wire.
IF still energized after that:
Need to look at elements. Best way is to remove blower housing and look down at elements from above with light.
See if one of them has fallen down and touching element frame.
Thanks,
Robert
First, be sure it isn't the t-stat by removing the W wire.
IF still energized after that:
Need to look at elements. Best way is to remove blower housing and look down at elements from above with light.
See if one of them has fallen down and touching element frame.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Thanks Robert, I found a broken heating element. I assume the end of it was dangling down and grounding out on the frame.
Thanks,
Greg Creech
Thanks,
Greg Creech
I tied it back together until I can get one and it works fine. What is the part # I need to order?
Hi Greg,
You're very welcome. You should have 3 coils, 2 on one assembly plate and one on the other.
Which coil is it ? The plate assembly has to be replaced, you cannot get just the one coil.
Is it the single coil assembly or one of the double coils ?
It would be best to disconnect the wires to the broken coil and go with the two remaining until replaced.
It will up the amps tying it together and can cause more damage and even become a fire hazard like that.
Thanks,
Robert
You're very welcome. You should have 3 coils, 2 on one assembly plate and one on the other.
Which coil is it ? The plate assembly has to be replaced, you cannot get just the one coil.
Is it the single coil assembly or one of the double coils ?
It would be best to disconnect the wires to the broken coil and go with the two remaining until replaced.
It will up the amps tying it together and can cause more damage and even become a fire hazard like that.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Question about burned wiring on e2eb-015ha
by thomasclay » Thu Sep 14, 2017 5:37 pm » in Nordyne Service & Repair - 0 Replies
- 60574 Views
-
Last post by thomasclay
Thu Sep 14, 2017 5:37 pm
-
-
- 0 Replies
- 72882 Views
-
Last post by newguy47
Thu Aug 16, 2018 8:21 pm
-
-
heater blower intertherm feh-015ha-03
by newguy47 » Wed Oct 24, 2018 8:04 am » in Nordyne Service & Repair - 0 Replies
- 79264 Views
-
Last post by newguy47
Wed Oct 24, 2018 8:04 am
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 155206 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Nordyne Mod. E1EH-015HA split unit/eliminate cooling?
by carolina jim » Thu Oct 24, 2019 8:33 am » in Nordyne Service & Repair - 0 Replies
- 35359 Views
-
Last post by carolina jim
Thu Oct 24, 2019 8:33 am
-