Miller Model P3RA-030K
A/C works great. Until yesterday morning the heater worked great also. All of a sudden I turn the heat side on and get cool air. I changed the thermostat, as it has been installed for many years. Before I call a tech and spend bunches of money is there anything I can check myself first? Since I'm in Central FL the heat isn't a really big deal, but would still like to have it working....you know, for those really cold days when it gets below 65.....
I haven't gotten into the unit yet to check it out. Where would the heat strips be located? Oh, and thanks for the rapid response....ED
Hi Ed,
Is the outside unit your only unit, no furnace in the home ?
If so, the heat strips will be inside the outside unit inside the half without the fan grille on top.
Look for a side door panel and should see electrical conduit entering in same area.
Thanks,
Robert
Is the outside unit your only unit, no furnace in the home ?
If so, the heat strips will be inside the outside unit inside the half without the fan grille on top.
Look for a side door panel and should see electrical conduit entering in same area.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi Ed,
Also, I'm going to move this over to the Nodyne forum as Miller is made by Nordyne.
Follow it over there please.
IF you have zero warm air, may be a tripped breaker or a bad contactor or loose wiring.
If partial, but low heat, may be contactor, loose wiring, bad element coil or bad limit switch.
Just some possibilities there.
Thanks,
Robert
Also, I'm going to move this over to the Nodyne forum as Miller is made by Nordyne.
Follow it over there please.
IF you have zero warm air, may be a tripped breaker or a bad contactor or loose wiring.
If partial, but low heat, may be contactor, loose wiring, bad element coil or bad limit switch.
Just some possibilities there.
Thanks,
Robert
Last edited by Robert on Sat Mar 01, 2008 7:13 am, edited 1 time in total.
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Thanks Robert. I'll get a chance this afternoon when I get off work to check it out. I'll let you know. It is outside with no furnace inside. ED
Hi Ed,
I found the data info on it after I wrote ya. See if you can tell how many KW it is, probably 8kw or 10kw.
Thanks,
Robert
I found the data info on it after I wrote ya. See if you can tell how many KW it is, probably 8kw or 10kw.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
I didn't check the kw, but found the problem. Now, at the risk of sounding like an idiot, here we go.......There are springs (coils), and several wires connecting to what looks to be diodes, like on the back of an auto alternator, that are plugged into the plate at the end of the springs. 2 of the wires are burnt thru. Looks like the whole assy. needs to be replaced. What is the assy called? Next, what would the wire gauge be of the 2 that are burnt so I can replace them? Hope I gave you enough info. I'm totally ignorant about HVAC, but am willing to learn....:0)
I just pulled a website for replacement parts and discovered it is the heating element (DUH)....now, where the wires are plugged into it, 2 of them are burnt thru, along with what I called a diode. I am assuming the whole element needs replaced. Also, the 2 wires, what guage? Thanks Robert....ED
Hi Ed,
I hope it was this website as we have an online store for replacement parts, the sale of which keeps these forums up and running.
Where the wires connect is basicly an insulator to the metal.
I will have to see if the assembly is still available or whether a restring kit is needed.
Usually the wire is 10AWG, but best to look at one not burnt to see for sure, wire size printed on the wires.
We either have in stock or can quickly get any parts needed that are available still.
For them to burn, you either had a high amperage draw or a loose connection.
Let me know on wire gauge and I will need to know kw rating to check for replacement.
Look for a model number or kw rating on the element assembly.
Thanks,
Robert
I hope it was this website as we have an online store for replacement parts, the sale of which keeps these forums up and running.
Where the wires connect is basicly an insulator to the metal.
I will have to see if the assembly is still available or whether a restring kit is needed.
Usually the wire is 10AWG, but best to look at one not burnt to see for sure, wire size printed on the wires.
We either have in stock or can quickly get any parts needed that are available still.
For them to burn, you either had a high amperage draw or a loose connection.
Let me know on wire gauge and I will need to know kw rating to check for replacement.
Look for a model number or kw rating on the element assembly.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Looks like the numbers on the element numbers are worn out, or close to it. I have to work a few hours this morning, then I'll try to make out the numbers, and the gauge on the wire. I looked closer yesterday evening and it looks like the element can be unplugged from the insulator. Other than the wires being burnt, the element looks to be in good shape. Oh, the unit has some moisture in the bottom, right below the element. Looks like the wires got wet....I'll get you to order those parts as soon as I get back to you...Thanks...ED
KW looks to be 9.6 on the element. Wire is 12 AGW. 2 insulators need replaced along with 2 wires. Wires are only about 4-5 inches long. Also need end terminal clips for both wires. Let me know if you need more info. Thanks...ED
I checked the element very closely and it looks like I need the whole thing. The element was broken on the end. If you can get the order info and price for me let me know so I can order it. Thanks. ED
Hi Ed,
Will have Mark check with distributors tomorrow and let you know tomorrow night or Tuesday at the latest. Monday's are always hectic as we receive orders through the w/e and they have to be processed on Mondays.
Thanks,
Robert
Will have Mark check with distributors tomorrow and let you know tomorrow night or Tuesday at the latest. Monday's are always hectic as we receive orders through the w/e and they have to be processed on Mondays.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi Ed,
How much wire do you need and do you also need high heat terminal connectors for the wire ?
Thanks,
Robert
How much wire do you need and do you also need high heat terminal connectors for the wire ?
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
have intertherm heat pump with a 913421 control box tying to a miller 841 thermo stat ,
by hillcat01 » Mon Oct 21, 2019 7:28 pm » in Nordyne Service & Repair - 0 Replies
- 86654 Views
-
Last post by hillcat01
Mon Oct 21, 2019 7:28 pm
-
-
-
I need wiring assistance for a miller furnace serial number A0981-0685
by Timodell » Wed Nov 20, 2019 10:40 pm » in Nordyne Service & Repair - 0 Replies
- 65448 Views
-
Last post by Timodell
Wed Nov 20, 2019 10:40 pm
-
-
-
Fluctuating flue draft Miller CMF2 80 PO CONV
by ctwap2783 » Sat Feb 22, 2020 9:36 pm » in Nordyne Service & Repair - 0 Replies
- 122719 Views
-
Last post by ctwap2783
Sat Feb 22, 2020 9:36 pm
-
-
- 0 Replies
- 131795 Views
-
Last post by wogman75
Tue Jul 28, 2020 2:43 pm
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 116274 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-