Stopped blowing hot air last night. Had got to the point it took a while to warm the trailer.
Was thinking I might need new coils.
Intertherm Central Electric Furnace
FEH-012HA
240v
60hz
1 phase
41,000 BTUH
12kw
Any help would be greatly appreciated.
Not a lot of money to spend either.
Intertherm FEH-012HA
Need to know if sequencer is sending signal to all elements and if so, are they working.
See if bottom H1/H2, H3/H4, etc are getting 24vac from t-stat.
If so, do you have 240vac at M1/M2, M3/M4, etc. ?
Thanks,
Robert
See if bottom H1/H2, H3/H4, etc are getting 24vac from t-stat.
If so, do you have 240vac at M1/M2, M3/M4, etc. ?
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
I've back tracked a little on the coils...
I did a little more trouble shooting last night and found that the NON-40 fuses were both brittle and broke when I removed them.
I have purchased new fuses (both Non-40 and Non-30 which are required) and will replace this evening.
I'm hoping this may be the fix, but I will let you know more later this evening.
I did a little more trouble shooting last night and found that the NON-40 fuses were both brittle and broke when I removed them.
I have purchased new fuses (both Non-40 and Non-30 which are required) and will replace this evening.
I'm hoping this may be the fix, but I will let you know more later this evening.
The fuses did the trick. Sweet heat.
Heat hasn't been this good in a couple of years.
Thanks for you help and I'm glad I found this site.
Heat hasn't been this good in a couple of years.
Thanks for you help and I'm glad I found this site.
-
- Similar Topics
- Replies
- Views
- Last post
-
- 0 Replies
- 77369 Views
-
Last post by newguy47
Thu Aug 16, 2018 8:21 pm
-
-
heater blower intertherm feh-015ha-03
by newguy47 » Wed Oct 24, 2018 8:04 am » in Nordyne Service & Repair - 0 Replies
- 83676 Views
-
Last post by newguy47
Wed Oct 24, 2018 8:04 am
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 164891 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
intertherm feh-015ha-04 Noisy Blower
by kjaxes99 » Sat Oct 24, 2020 4:45 am » in Nordyne Service & Repair - 0 Replies
- 139685 Views
-
Last post by kjaxes99
Sat Oct 24, 2020 4:45 am
-
-
-
Intertherm FEH-017HAC won't shut off
by Jetherid » Mon Dec 07, 2020 6:22 pm » in Nordyne Service & Repair - 0 Replies
- 172686 Views
-
Last post by Jetherid
Mon Dec 07, 2020 6:22 pm
-