Post all other heating and cooling questions here.

Moderators: Greg, Mark

Locked
Suefie
Posts: 1
Joined: Fri Oct 15, 2010 2:46 pm

I have a no heat situation with my Miller furnace in my 4 year old manufactured home, model #M3RL080ABW. Since replacing thermostat, furnace will not come on. The programmable thermostat has been tested and it is good and wired correctly. Even when reinstalling the manual stat, no heat. Furnaces transformer is humming. Suggestions would be greatly appreciated.
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Test transformer for proper voltage. Line/Primary side = 120vac. Load/Secondary side = 24vac.

Real easy to blow a transformer when wiring a t-stat if not careful. Or could have just went bad at that time.



Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?