Post all other heating and cooling questions here.

Moderators: Greg, Mark

Locked
Tim M
Posts: 28
Joined: Thu Mar 15, 2007 1:10 am

I have what looks like about a 4" space around the vent pipe itself as it goes thru the ceiling. I have noticed an immense amount of heat pours down thru this during the summer. Does this cause a loss in the efficiency of my cooling with A/C? If so...what do you recommend? I have a Coleman Presidential model.
User avatar
hvac1000
Posts: 292
Joined: Wed Feb 28, 2007 9:19 am
Location: Cincinnati ohio

Usually this pipe will have a metal collar where it makes the penetration at the ceiling. You can cut a circle out of a metal piece then cut it in half. This will allow you to install it without removing the pipe. I would like to see a picture if you can post one.

What ever you end up doing do not use any combustible material to close this gap.
God, grant me the serenity
to accept the things I cannot change;
the courage to change the things I can;
and the wisdom to know the difference.
Tim M
Posts: 28
Joined: Thu Mar 15, 2007 1:10 am

There doesn't seem to be any insultion close to the pipe. Would it hurt to stuff some in there (with out the paper of course)?
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Go to this page and scroll down to locate:

http://www.mobilehomerepair.com/ColemanChimneys.html


Ceiling Ring # 7660-2841 @ $9 + $4.50 shipping.

It can be ordered from there through Paypal or by calling toll free to

1-877-263-7860 and charging to Visa or Mastercard.


Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?