Hello,
Hoping someone can help me out on this. My Thermostat clicks and calls for heat but my furnace doesn't do anything. I tried jumpering to see if I can get any activitiy but I was only able to get the blower to turn on. My pilot is lit, seems all the wiring is in place. The furnace is a Intertherm, older guy Any help is greatly appreciated. Thanks

Re: Furnace not turning on

Posted: Sat Oct 13, 2012 11:13 am
by 1987Commodore
First, is the knob on the gas valve set to "pilot," or "on" ?






'

Re: Furnace not turning on

Posted: Sat Oct 13, 2012 12:45 pm
by Kennyy7
The knob is in the ON position.

Re: Furnace not turning on

Posted: Sat Oct 13, 2012 10:38 pm
by ponch37300
First, what is the make and model of the furnace and how old is it?

After the thermostate clicks nothing at all happens? No booster blower? Does your furnace have status lights, usually green and either steady or blinking? Is your furnace getting electricity, maybe breaker tripped or something? Just trying to throw out some ideas to check.

Re: Furnace not turning on

Posted: Mon Oct 15, 2012 11:50 pm
by DaleM
Model number really helps. If you have an older pilot model with no booster motor then here's a few things to try. When you have the power on and tstat calling for heat see if you have 24 volts at the control/gas valve. If no voltage then something is bad in the low voltage wiring.

(((QUICK CHECK!! With power off look for any resettable limit switches. Look on left side of blower assembly and below burner intake assembly. Usually a red or brown button right in the middle of them, push it in to reset.)))

If still nothing, kill power, take the red and white wires apart from the thermostat wires at the furnace. Twist red and white wires from the furnace together, this will eliminate the thermostat and wiring to it as a problem. Turn power on, furnace should fire, again if nothing check voltage at the control/gas valve. If voltage is there, turn off power and gas and pull burner assembly. Remove pilot tube and thermocouple, pull oriface from end of burner tube, it's a little brass thingy with a hole in it. Look into oriface to be sure it is clear and then look into burner tube down into the control valve. It should be clear. If you see white in there you need to clean the web out of the tube. Use a Qtip to do this. Put it all back together and give it a try.

If there is no web I would say the control valve is bad and should be replaced.