2006 Intertherm tripping Vent Temp Switch

Questions about repairs and parts for Nordyne furnaces, air conditioners and heat pumps for manufactured homes including Intertherm, Mac and Miller brands. Click here for Nordyne parts.

Moderators: Greg, Mark

Locked
Dwight
Posts: 1
Joined: Mon Oct 08, 2012 2:12 pm

I have an Intertherm Model M3RL060A BWT, Serial M3A0600203233. The Temp Switch on the recirculation blower keeps tripping. The switch is a 145 degree, I bought a replacement and the new one trips even more often. I read on here about the problems with the restrictor orifice on the 2007 models, so I pulled the recirculation fan and found no restrictor at all. I have included photos of the blower back and mounting surface.

Looking for next step suggestions.

Thanks,
Dwight
You do not have the required permissions to view the files attached to this post.
DaleM
Posts: 385
Joined: Wed Apr 07, 2010 10:07 am

I have seen restrictors that have gone bad but never one missing all together. I would say get the proper restrictor for your furnace, install it and see if that takes care of the problem. That restrictor should be in there.