nordyne e1eb-015ha heat will not cut off

Questions about repairs and parts for Nordyne furnaces, air conditioners and heat pumps for manufactured homes including Intertherm, Mac and Miller brands. Click here for Nordyne parts.

Moderators: Greg, Mark

Locked
tross
Posts: 2
Joined: Sun Jan 01, 2012 8:36 pm

This unit heating will not cut off. The T stast has been replaced and the fan relay also been replaced. The breaker would have to be turned off before the unit will cut off.
First time he turn breaker off and then back on and it worked good for days then would not cut off. Replaced Tstast and it worked good for about a week then started not working again. So replaced fan relay and worked fine for 2 days, Tonight it stuck on again. Need some help . Thanks Todd
User avatar
flcruising
Posts: 606
Joined: Mon Dec 03, 2007 2:18 pm
Location: Florida Panhandle

Does the unit respond to the t-stat at all - HEAT/COOL or Fan ON/AUTO?
[color=blue]Aaron[/color]
tross
Posts: 2
Joined: Sun Jan 01, 2012 8:36 pm

yes it dose and will work fine for a day or so. Even if the stast tells it to cut off it wll not. heater and blower still run until all power to unit is killed. looks like the sequenceris sticking on and that is also holding the fan on also. Have two on order will try that. Thanks Todd
User avatar
flcruising
Posts: 606
Joined: Mon Dec 03, 2007 2:18 pm
Location: Florida Panhandle

I concur. Sequencer(s) sounds like the culprit.
[color=blue]Aaron[/color]