Intertherm E2EB-023HA

Postby cjrowles » Wed Jul 07, 2010 1:41 pm

Hello I have a E2EB-023HA ac/furnace setup. The problem is that the blower runs continuously even when the outside unit is off. It has to be shut off at the breaker box or the breaker on the blower its self. What would cause this? Thanks
cjrowles
 
Posts: 1
Joined: Wed Jul 07, 2010 9:24 am

Re: Intertherm E2EB-023HA

Postby Robert » Thu Jul 08, 2010 1:20 am

Hi,

Most often that would be due to a sticking fan relay.

Relay # 621867 can be seen and ordered from here by scrolling down page to it :

http://www.aberdeenhomerepair.com/store ... ay-01-0157



Thanks,
Robert