Hello,
I have a few questions about an electric furnace, Nordyne model E2-015 HA.
I purchased a mobile home with this unit. I only want to hook up the heater at the present time, my problem is the previous owner took all the circuit breakers out of the house when he left. I have replaced all except the ones for the heating unit. The outside A/C unit is not connected and I don't intend to use it .
The heating unit has 60 amp breakers on the bottom of the unit itself. One set is connected to 2 ea. #6 wires and the second is for 2 ea. #10 wires.
My questions are.

1 Are these two sets of wires all that should be coming to the heating unit ?

2 What size breakers do I need for my house breaker box? for the #6 wires and then for the #10 wires?
I am thinking 60 amp for the #6 and 30 amp for the #10.


thanks,
Dean
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,


1- Yes

2- Correct, 60A for #6 and 30A for #10 (Make sure they are over-current breakers).




Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Dean33
Posts: 8
Joined: Thu Aug 27, 2009 3:39 pm

Robert,
I now have heat, much obliged.
Dean
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi Dean,

You're very welcome, happy to help.



Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Dean33
Posts: 8
Joined: Thu Aug 27, 2009 3:39 pm

Hi Robert,
The fan runs at a higher speed on ventilation and a lower speed on heat, is that normal?
thanks again,
Dean
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi Dean,

Yes.

Cooling = High speed

Fan ON (Continuous) = High speed

Heating = Low speed or Med. Low depending on furnace




Thanks,
Robert