Was working fine now it won't turn on at all. Have a Honeywell RTH 230B thermostat less than 6 mos old.
It shows the flame icon when you set it for heat and the snowflake when it's set for cool, but nothing happens.
Ser# P3B020802015, if you need it.
Ideas? Thanks.
Ross
Nordyne-P3RC036K-won't turn on heat or cool
Hi,
Nothing will come on except when t-stat is set for Cool. Go outside to A/C unit and look closely to see if the t-stat wire coming from home to unit has been pulled loose or chewed through.
If you have a meter, test across Contactor side coil terminals for 24-28vac.
Inside at t-stat, remove cover(s) and see if you have 24-28vac across the R and Y terminals.
Take care and best wishes,
Robert
Nothing will come on except when t-stat is set for Cool. Go outside to A/C unit and look closely to see if the t-stat wire coming from home to unit has been pulled loose or chewed through.
If you have a meter, test across Contactor side coil terminals for 24-28vac.
Inside at t-stat, remove cover(s) and see if you have 24-28vac across the R and Y terminals.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Robert, thanks for the reply. It works! Did as you said, chkd for 24 volts etc. Got zero. then chkd for 240 v, got zero.
Went out to the main, 240v into the breakers zero out. Looked at the breakers before and they were on, still looked like it. Flipped them off & on & voila, it works.
A duh...on my part. Never thought to check the most basic thing of all.
Thanks again!
Ross
Went out to the main, 240v into the breakers zero out. Looked at the breakers before and they were on, still looked like it. Flipped them off & on & voila, it works.
A duh...on my part. Never thought to check the most basic thing of all.
Thanks again!
Ross
Robert, one more bit of info. The circuit breaker, on an outside pole, tripped again "after" the air con shut off. It only did that the first time, after I flipped the breakers and has been fine since. Maybe a possible problem with the circuit breaker or something in the Nordyne?
Wife mentioned it did the same thing when we had the heat on. That was the last time the unit worked untill I flipped the breakers today.
Thanks again,
Ross
Wife mentioned it did the same thing when we had the heat on. That was the last time the unit worked untill I flipped the breakers today.
Thanks again,
Ross
Hi Ross,
Wouldn't hurt to replace the circuit breaker, they do sometimes go bad.
Also could be a loose lug at main power connection in service panel box on pole.
Be VERY careful out there, alot of people have been seriously injured or killed at those poles.
To know more would require checking amperage draws and thoroughly testing circuit.
IF there's any problem with the unit itself, a top suspect would be the compressor.
Take care and best wishes,
Robert
Wouldn't hurt to replace the circuit breaker, they do sometimes go bad.
Also could be a loose lug at main power connection in service panel box on pole.
Be VERY careful out there, alot of people have been seriously injured or killed at those poles.
To know more would require checking amperage draws and thoroughly testing circuit.
IF there's any problem with the unit itself, a top suspect would be the compressor.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi Robert,
Thanks for further tips....and yes, I will be very careful with the high voltage....don't want to get welded!
So far, the breaker hasn't tripped.
Ross
Thanks for further tips....and yes, I will be very careful with the high voltage....don't want to get welded!
So far, the breaker hasn't tripped.
Ross
Hi Ross,
That's great, hopefully it will continue to stay online. Thanks for update.
Take care and best wishes,
Robert
That's great, hopefully it will continue to stay online. Thanks for update.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 142347 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
swamp cooler in hallway, how to get the rest of my mobile home cool?
by grateful » Mon May 25, 2020 7:30 pm » in All Other HVAC Questions - 0 Replies
- 87973 Views
-
Last post by grateful
Mon May 25, 2020 7:30 pm
-
-
-
In too deep to turn back now... now what?
by Do it herselfer » Thu Nov 02, 2017 11:28 pm » in Mobile Home Repair - 2 Replies
- 23233 Views
-
Last post by yakima4$
Tue Dec 05, 2017 8:29 pm
-
-
- 2 Replies
- 14430 Views
-
Last post by TorstenW
Tue Mar 06, 2018 1:04 am
-
-
Intertherm FEH-017HAC won't shut off
by Jetherid » Mon Dec 07, 2020 6:22 pm » in Nordyne Service & Repair - 0 Replies
- 146025 Views
-
Last post by Jetherid
Mon Dec 07, 2020 6:22 pm
-