Nordyne m1gb 056a bw furnace
Posted: Sat Dec 06, 2008 4:50 pm
by shenry
My problem is after the burner lights it appears as if it is getting blown out before the blower comes on, could this be caused by a down draft or what. I am puzzled. Thanks in advance for any help you can give.
Sam H.
RE: Nordyne m1gb 056a bw furnace
Posted: Sat Dec 06, 2008 10:53 pm
by Robert
Hi Sam,
Could be, but hard to say without being there. Have you checked to see if roofjack weather cap is still there or did it have one ?
Does roofjack extend above the roof peak ?
Thanks,
Robert
RE: Nordyne m1gb 056a bw furnace
Posted: Sun Dec 07, 2008 2:25 pm
by shenry
Robert
The cap is on but it is one that I put on when bought the mobile home , because the old one was missing . It does not extend above the roof peak , is it supposed to. I left out in my previous post that I have already replaced the gas valve and the thermocouple trying to fix this problem.
Thanks again for the help
Sam H.
RE: Nordyne m1gb 056a bw furnace
Posted: Mon Dec 08, 2008 2:41 am
by Robert
Hi Sam,
Yes, it should extend above the roof peak.
Also, be sure the cap is an all weather cap.
Thanks,
Robert