Miller (Nordyne)#Q3RC won't start (intermittent)
Hello: I have an older Miller #Q3RC Heat Pump here in FL that very occasionally will not start in AC mode. As an example, upon returning recently here to FL after about 6 months, the house temperature inside was at 89 with the thermostat set at 80. Cycling the thermostat up & down would not start it. I then cycled the main A/C breaker off, then on again and the unit started up and has been running fine for the last 5 days straight. This heat pump has done this 2 or 3 times in the past and has always restarted each time by cycling the main A/C breaker. The next time this happens, I plan to leave it off so that proper troubleshooting can be done. I was wondering if you had any ideas in the meantime as to what might be the cause of this problem? Also, what should be checked if/when my heat pump is in this condition again ? I also have a question re: the operation of this system! Should the air handler blower continue to run for a fixed time, after the compressor cycles off, to gain that last bit of "cold" from the "A" coil ? This system (blower, fan & compressor) shuts down completely immediately after the thermostat "clicks" off. I have a newer A/C system "up North" that does run for approx. 1 min. after the compressor cycles off, but that is not a heat pump. Thanks for any information you can provide. Ray in sunny FL.
Hi Ray,
I would start by checking the breaker, then transformer, t-stat, a/c condenser contactor for voltage in and out.
Since resetting breakers cures it, breaker may be weak and going bad.
To have blower remain on for short period, it must be built into t-stat, control board or have a relay installed for that purpose.
Thanks,
Robert
I would start by checking the breaker, then transformer, t-stat, a/c condenser contactor for voltage in and out.
Since resetting breakers cures it, breaker may be weak and going bad.
To have blower remain on for short period, it must be built into t-stat, control board or have a relay installed for that purpose.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi Ray,
You're very welcome, happy to help. Holler if it happens again and let me know what you found.
Thanks,
Robert
You're very welcome, happy to help. Holler if it happens again and let me know what you found.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 14 Replies
- 161716 Views
-
Last post by Greg
Tue Sep 26, 2017 1:00 pm
-
-
3500A816 Randomly wont start or shut down
by Smithcraft » Fri Jan 13, 2023 4:04 pm » in Coleman Service & Repair - 0 Replies
- 94898 Views
-
Last post by Smithcraft
Fri Jan 13, 2023 4:04 pm
-
-
-
have intertherm heat pump with a 913421 control box tying to a miller 841 thermo stat ,
by hillcat01 » Mon Oct 21, 2019 7:28 pm » in Nordyne Service & Repair - 0 Replies
- 86598 Views
-
Last post by hillcat01
Mon Oct 21, 2019 7:28 pm
-
-
-
I need wiring assistance for a miller furnace serial number A0981-0685
by Timodell » Wed Nov 20, 2019 10:40 pm » in Nordyne Service & Repair - 0 Replies
- 65402 Views
-
Last post by Timodell
Wed Nov 20, 2019 10:40 pm
-
-
-
Fluctuating flue draft Miller CMF2 80 PO CONV
by ctwap2783 » Sat Feb 22, 2020 9:36 pm » in Nordyne Service & Repair - 0 Replies
- 122676 Views
-
Last post by ctwap2783
Sat Feb 22, 2020 9:36 pm
-