Coleman pres II furnace/thermostat issue?

Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
technodude60
Posts: 8
Joined: Fri Nov 26, 2010 2:22 am

Fri Nov 26, 2010 3:02 am

HELP! :cry: I am not a guru when it comes to HVAC problems so here goes.
I am replacing the old honeywell round style thermo with a new digital one. It's a Hunter 44155c on a Coleman presidential II furnace in a older mobile home.
First off I have no idea,nor how to tell if this unit has a heat pump. I have installed the new hunter thermostat and the furnace will cycle on for 30 sec and off again. Temp is set to 68 and temp does not seem to go up. This unit IS working when a/c is on however.
Settings are as follows;
Thermo switches in the back are; STD/HP- on STD
Recovery- enable on
Fan - HG/HE- on HG

Wiring; G-grn
RC-jumpered with RH
RH-red
Y/O-dark green
W/B- white
Y1- no connect

I'm not sure what else I can add? I've read a little about the fan limit switches but I'm not sure where they are,or info on if there is a heat pump?
I have no diagrams/schematics as this would help!
Any ideas? Help!
Thanks in advance!
John


User avatar
Greg
Moderator
Posts: 5378
Joined: Wed Feb 28, 2007 8:01 pm
Location: Weedsport, NY
Contact:

Fri Nov 26, 2010 8:14 am

Lets get this moved to the heating section. Greg
"If I can't fix it, I can screw it up so bad no one else can either."

technodude60
Posts: 8
Joined: Fri Nov 26, 2010 2:22 am

Fri Nov 26, 2010 10:20 am

I thought I did post this in the heating / Coleman section?
?????

John

User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Fri Nov 26, 2010 6:23 pm

Hi,

First, I would return the heat pump t-stat and get one for your a/c and furnace that is not for heat pumps.

Next, I would not get a Hunter, I would get a Honeywell or a RiteTemp.


Then I would trace the dark green back to furnace and see where it goes. May want to clean it off and see if it is really dark green.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?

technodude60
Posts: 8
Joined: Fri Nov 26, 2010 2:22 am

Sat Nov 27, 2010 3:34 am

Thanks for the reply robert. I checked the book again for the hunter 44155c thermostat,and it states single stage heat pump- no aux.
Not designed for multi stage heat pump systems. Our coleman pres. II doesn't have a heat pump.
Is this thermostat still the wrong model? The dark grn wire I believe is from the compressor. This unit did work with the a/c on,but just turns on/off for no more than 30 sec increments even when set to "span3"
Thanks for your help again robert!
John


User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Sat Nov 27, 2010 10:50 pm

Hi John,

Yes, it is a heat pump t-stat and you do not have a heat pump.



Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?

technodude60
Posts: 8
Joined: Fri Nov 26, 2010 2:22 am

Sun Nov 28, 2010 10:42 am

Robert,
I failed to mention before that this furnace is the coleman presII Model 7600B.
I disconnected the hunter stat and bought a simple honeywell digital without the program feature and installed it last night. This honeywell is the model RTH111B. The furnace is still short cycling and will not stay on. I called a buddy of mine who used to have a mobile home with a coleman furnace,he said to look for a resettable limit switch on the top side of the blower housing? I saw a switch but it did not have the reset button. I did NOT take off the metal cover where the other components are,but I do have a vom and the schematic is on the cover.
Could there be a switch in there maybe?
Thanks!
John

gordo48111
Posts: 67
Joined: Fri Nov 12, 2010 10:45 am

Sun Nov 28, 2010 12:45 pm

John,

Was it cycling ok this season with the old t-stat? If so, try reinstalling it and see what happens. Make sure the connections are correct. If you indeed do have a dark green wire that powers the outdoor condensing unit, it should be on Y or Y1. It may actually be blue and normally would be yellow. Are there any unused stat wires?
"Man...that blowed up real good!"

technodude60
Posts: 8
Joined: Fri Nov 26, 2010 2:22 am

Sun Nov 28, 2010 2:22 pm

We changed the old round stat because the a/c quit. We installed the hunter stat then the a/c worked again,lol! So I guess we change stats with the season,huh?
Yes,the supposed dk. green wire is really blue. There is only a total of 4 wires. Red,green,white and blue,all connected. So now we have a no frills,non-prog. dig dispay honeywell model RTH 111B installed. We have no heat pump that I'm aware of.
ARRRRGGGGHHH!

John.

gordo48111
Posts: 67
Joined: Fri Nov 12, 2010 10:45 am

Sun Nov 28, 2010 3:34 pm

So...the heat has not cycled properly at all since you replaced the t-stat, is that correct? Coincidental for sure. The RTH111B is not designed for a heat pump application. If you had a heat pump the outdoor unit would run during the heating cycle as well as the cooling cycle. As you did with the Hunter t-stat, read the instructions again to see if any DIP switches need to be set in another position - i. e. cycle rate for forced air gas (FG), fan - gas heat, etc. The next thing(s) to check would be the temperature rise across the heat exchanger. If it is too high (>70 degrees)the limit could be opening and closing which would cycle the burner off and on but the blower would continue to run. If this is the case check filters, blower wheel for dirty vanes, cooling coil for dirt-clogged fins and blower RPM. If the temperature rise checks out ok then ohm out the limit when the furnace cycles off. Disconnect power to the furnace and remove one wire from the limit when testing. If it is open when the furnace shuts down and closes after cooling off, with all other operations ok, replace the limit. There could be one on the wall of the combustion chamber and one in the blower compartment. If the limits are not open when the furnace shuts down it could be the t-stat, control board, or other problem that may require a tech to investigate. Robert should be back soon to add his expertise to your situation. I do have 25 years experience in residential/commercial/industrial HVAC/R but he no doubt has seen more Colemans than I have.
"Man...that blowed up real good!"

technodude60
Posts: 8
Joined: Fri Nov 26, 2010 2:22 am

Sun Nov 28, 2010 4:59 pm

There is only one jumper in the back of this honeywell stat which switches the fan from gas to electric which is set on HG for gas.
Thanks for your help. I think this may be over my head.

John

User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Mon Nov 29, 2010 3:52 pm

Hi John,

Some of the Hunter t-stats have to be set to HG for use with an electric furnace. So, set it to HE and see what happens.

If still the same, then it will take a total testing of each cycle and sequence to see what's up.


What is complete furnace model number just to be sure I have it.

I'm going to read all again and see if I missed anything.

I also do offer a email troubleshooting session one on one for a $20 fee IF you think it may help.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?

technodude60
Posts: 8
Joined: Fri Nov 26, 2010 2:22 am

Mon Nov 29, 2010 11:36 pm

I installed a new honeywell stat as you suggested. The model RTH111B is inline with our Coleman PresII, model 7600B.
Thanks for the offer robert but I don't see how you could help further,unless you were here looking at it in person. Even with the new honeywell,the fan comes on from 30-45seconds. The pilot is on,but no heat.

John.

User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Tue Nov 30, 2010 6:09 am

Hi John,

Then the t-stat is not the problem and circuits will have to be tested with meter to find the fault.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?

gordo48111
Posts: 67
Joined: Fri Nov 12, 2010 10:45 am

Wed Dec 01, 2010 6:34 am

John,

It would have helped if you had mentioned earlier that it was only the blower that was short cycling but no heat. You first said that the furnace wouldn't stay on. Big difference.
"Man...that blowed up real good!"