Hi guys,
New to the site and I love the forum. My electric furnace has 2 circuit breakers on the front of the unit and one keeps shutting off and consequently shuts down the unit after operating for around 10-15 minutes. I reset the breaker and it does the same thing, usual heat and air flow but just shuts off the breaker closest to the outside face of the unit. The other side doesn't kick off. From what I read, these control the heating elements. Does this signify a bad element or a bad breaker, or some other issue with the blower motor or something else? Any help would be appreciated. Thanks
Dan
Coleman Presidential Model 6806 A 842 circuit breaker ???
Hi Dan,
If original, probably a bad breaker or problem with furnace wiring.
Most likely the breaker though.
Thanks,
Robert
If original, probably a bad breaker or problem with furnace wiring.
Most likely the breaker though.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Posts: 5
- Joined: Sun Jan 03, 2010 11:31 pm
Thanks for the response, Robert. It is original from what I can tell and makes the most sense. Do you happen to know what that particular breaker is for? We installed a digital thermostat last year and I was suspicious that might have something to do with it. Thanks!
Humbly Greatful,
Dan
Humbly Greatful,
Dan
Hi Dan,
They are for shutting down power to work on furnace if there is a problem with components or wiring. The t-stat would not cause that.
Thanks,
Robert
They are for shutting down power to work on furnace if there is a problem with components or wiring. The t-stat would not cause that.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Posts: 5
- Joined: Sun Jan 03, 2010 11:31 pm
Robert,
After looking at the breakers/wiring in question, next I pulled the lower front cover off to check the wiring and the wires coming from one of the sequencers look like they got hot at some point and there was some black sooty residue on the inside of that cover where the sequencers are. Near the connections on the #1 sequencer appears to be the hot spot. All the wires from #2 sequencer appear fine and are not melted or anything. There is a wiring diagram on the inside of the upper cover that shows how those are wired and that sequencer is wired to elements #1 and #2. I'm assuming the sequencer controls the elements, and this setup is wired to those breakers above so this may be the source of the problem. Not to jump ahead of myself too soon, but if I change out the sequencers, should I change all the elements as well? (I really like to do things right the first time, and I hate having parts break down one after the other...) I haven't done this before but I have read the information available on your site and I know I can do it. I can send you pictures if that will help you out if I am not clear enough, just let me know when you have a chance. Thanks a million!
Dan
After looking at the breakers/wiring in question, next I pulled the lower front cover off to check the wiring and the wires coming from one of the sequencers look like they got hot at some point and there was some black sooty residue on the inside of that cover where the sequencers are. Near the connections on the #1 sequencer appears to be the hot spot. All the wires from #2 sequencer appear fine and are not melted or anything. There is a wiring diagram on the inside of the upper cover that shows how those are wired and that sequencer is wired to elements #1 and #2. I'm assuming the sequencer controls the elements, and this setup is wired to those breakers above so this may be the source of the problem. Not to jump ahead of myself too soon, but if I change out the sequencers, should I change all the elements as well? (I really like to do things right the first time, and I hate having parts break down one after the other...) I haven't done this before but I have read the information available on your site and I know I can do it. I can send you pictures if that will help you out if I am not clear enough, just let me know when you have a chance. Thanks a million!
Dan
Hi Dan,
This is the route most take in your situation with that age furnace.
Sequencer # 3120A3571 @ $53.54
24501 Restring Kit 5KW ( 4 ) @ $29.00 each X 4 = $116.00
Limit Switch # 6806 - 3351 ( 4 ) @ $18.43 each X 4 = $73.72
That sequencer is for a modern Coleman Electric Furnace of 20KW/4 coil variety.
The restrings are 5kw each giving same kw as now.
The limits are the actual OEM limits for your furnace.
All can be seen and ordered through PayPal from this page here :
http://www.mobilehomerepair.com/ColemanElec.html
THEN, continue shopping and go here for any wires or quick connectors needed:
http://www.mobilehomerepair.com/FurnaceElec.html
Those are high heat wires and connectors. I would go with the 10awg wire.
With new coils, sequencers, limits and wire/connectors, should be ok.
Those sequencers control the elements and the first set, M1-M2 also control the blower for heat mode.
Thanks,
Robert
This is the route most take in your situation with that age furnace.
Sequencer # 3120A3571 @ $53.54
24501 Restring Kit 5KW ( 4 ) @ $29.00 each X 4 = $116.00
Limit Switch # 6806 - 3351 ( 4 ) @ $18.43 each X 4 = $73.72
That sequencer is for a modern Coleman Electric Furnace of 20KW/4 coil variety.
The restrings are 5kw each giving same kw as now.
The limits are the actual OEM limits for your furnace.
All can be seen and ordered through PayPal from this page here :
http://www.mobilehomerepair.com/ColemanElec.html
THEN, continue shopping and go here for any wires or quick connectors needed:
http://www.mobilehomerepair.com/FurnaceElec.html
Those are high heat wires and connectors. I would go with the 10awg wire.
With new coils, sequencers, limits and wire/connectors, should be ok.
Those sequencers control the elements and the first set, M1-M2 also control the blower for heat mode.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 138761 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
LOUD Blower on Coleman Presidential 2 900759
by AuntKatie » Thu Apr 05, 2018 6:50 pm » in Coleman Service & Repair - 0 Replies
- 35038 Views
-
Last post by AuntKatie
Thu Apr 05, 2018 6:50 pm
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 97105 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Nordyne model m1mb 070a bw power issue
by Combustibleink » Mon Nov 16, 2020 10:21 am » in Nordyne Service & Repair - 0 Replies
- 94772 Views
-
Last post by Combustibleink
Mon Nov 16, 2020 10:21 am
-
-
-
Evcon Heat Pump - Air Conditioner Model No. BRHS036B Making HUM Before Starting
by Dave_L » Tue Aug 29, 2023 1:26 am » in Coleman Service & Repair - 0 Replies
- 99750 Views
-
Last post by Dave_L
Tue Aug 29, 2023 1:26 am
-