Coleman Evcon DGAT070BDD ignition failure : SOLVED

Posted: Sun Oct 25, 2009 9:15 pm
by ejvogie
I'm getting 1 blinking light, and when I look through the window into the furnace, I can see it's definitely not lighting. I don't see any glow at all. I also detect a faint gas odor when it tries to ignite. The heat exchanger has been replaced via the recall program. Any help appreciated, thanks in advance!

Re: Coleman Evcon DGAT070BDD ignition failure

Posted: Mon Oct 26, 2009 2:18 am
by Robert
Hi,

Disconnect connector where the two wires come to from the ignitor inside furnace.

Place meter leads into the furnace end of plug, set t-stat to call for heat and watch and see if after about a minute or so, you read 120VAC for about 35 seconds.


IF you do, ignitor is most likely bad.


Let me know what you read and will give ordering info if needed.


Thanks,
Robert

Re: Coleman Evcon DGAT070BDD ignition failure

Posted: Mon Oct 26, 2009 2:13 pm
by ejvogie
Multimeter is reading right around 120VAC.

Re: Coleman Evcon DGAT070BDD ignition failure

Posted: Mon Oct 26, 2009 5:44 pm
by ejvogie
Picked up an ignitor, problem solved. Thanks again!

Re: Coleman Evcon DGAT070BDD ignition failure : SOLVED

Posted: Mon Oct 26, 2009 7:19 pm
by Robert
Hi,

You're very welcome, happy to help.



Thanks,
Robert