Coleman Evcon DGAT070BDD ignition failure : SOLVED

Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
ejvogie
Posts: 3
Joined: Sun Oct 25, 2009 9:10 pm

I'm getting 1 blinking light, and when I look through the window into the furnace, I can see it's definitely not lighting. I don't see any glow at all. I also detect a faint gas odor when it tries to ignite. The heat exchanger has been replaced via the recall program. Any help appreciated, thanks in advance!
Last edited by ejvogie on Mon Oct 26, 2009 5:45 pm, edited 1 time in total.
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,

Disconnect connector where the two wires come to from the ignitor inside furnace.

Place meter leads into the furnace end of plug, set t-stat to call for heat and watch and see if after about a minute or so, you read 120VAC for about 35 seconds.


IF you do, ignitor is most likely bad.


Let me know what you read and will give ordering info if needed.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
ejvogie
Posts: 3
Joined: Sun Oct 25, 2009 9:10 pm

Multimeter is reading right around 120VAC.
ejvogie
Posts: 3
Joined: Sun Oct 25, 2009 9:10 pm

Picked up an ignitor, problem solved. Thanks again!
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,

You're very welcome, happy to help.



Thanks,
Robert