Furnace - Central Electric - Model # EB15B

Posted: Tue Mar 10, 2009 1:40 pm
by swr470
The blower motor runs continuously. I have to turn it off at the breaker. The heating unit kicks on and off at the correct temperature, but the blower never stops. Please help.....this is killing my monthly electric bill :!: :!: :!:

Posted: Tue Mar 10, 2009 2:17 pm
by Mark
Hi,

Just the blower running wouldn't run up the electric bill a whole lot, so you must also have one element not turning off either. To fix this, replace the sequencer. For your furnace, that is part number 3115-3571. It can be seen and ordered on this page of our website: http://www.mobilehomerepair.com/ColemanElec.html

Thanks,
Mark

RE: Furnace - Central Electric - Model # EB15B

Posted: Tue Mar 10, 2009 11:07 pm
by swr470
I will order the recommended part. Thanks Mark.

RE: Furnace - Central Electric - Model # EB15B

Posted: Fri Apr 24, 2009 1:55 pm
by swr470
installed the sequencer as suggested. Blower motor still runs.......any other suggestions :?:

RE: Furnace - Central Electric - Model # EB15B

Posted: Mon May 04, 2009 4:16 pm
by Robert
The sequencer controls the blower motor for heating mode.


Will need to test circuit to motor to find where it is being energized from.


Also, doublecheck sequencer wiring and make sure motor is wired from output side of M1 and M2.



Thanks,
Robert