Page 1 of 1

Coleman furnace model 7656b

Posted: Thu Dec 27, 2007 10:49 pm
by fordlover35
I have a coleman model 7656b in my home. the blower will come on and run for five mins then shut off, it also squeaks a lot. can anybody please help me try and fix it. thank you

RE: Coleman furnace model 7656b

Posted: Thu Dec 27, 2007 11:31 pm
by Robert
Hi,

What is last 3 digits of furnace model number such as 7656B856 ?


Have you cleaned and serviced motor recently or at all ?


Thanks,
Robert

RE: Coleman furnace model 7656b

Posted: Thu Dec 27, 2007 11:49 pm
by fordlover35
yes i have. the last three are 856

RE: Coleman furnace model 7656b

Posted: Fri Dec 28, 2007 12:08 am
by Robert
Is the motor HOT when it shuts off like this ?

Can you spin the wheel several revolutions at this time ?


Have you removed and inspected it ?


Could be motor, run capacitor, fan switch or a wiring problem.



Thanks,
Robert

RE: Coleman furnace model 7656b

Posted: Fri Dec 28, 2007 12:18 am
by fordlover35
yes the motor is very hot. you can spin the wheel but it does take a lil bet of effort to do it.

RE: Coleman furnace model 7656b

Posted: Fri Dec 28, 2007 12:22 am
by Robert
That sounds like a possible bearing seizing up. If so, motor is overheating and shutting down.


Is the motor getting full 120 volts to the wires going to motor ?


Do you have heat only or heat & a/c ?



Thanks,
Robert

RE: Coleman furnace model 7656b

Posted: Fri Dec 28, 2007 12:32 am
by fordlover35
its jsut heat. i am going to test to see if it is getting 120 volts tommorrow

RE: Coleman furnace model 7656b

Posted: Fri Dec 28, 2007 12:41 am
by Robert
Ok, just let me know and I'll help as much as possible.


Thanks,
Robert

RE: Coleman furnace model 7656b

Posted: Fri Dec 28, 2007 10:22 am
by fordlover35
yes it is getting 120 volts to the motor.

RE: Coleman furnace model 7656b

Posted: Sat Dec 29, 2007 7:20 am
by Robert
With 120vac getting to motor, it being HOT when it turns off early, wheel being hard to turn and it making sounds, most likely seized bearings .


Will be back in office later this evening if you would like a price quote and ordering info for a new motor.


Is it heat only or heat and a/c unit ?



Thanks,
Robert

RE: Coleman furnace model 7656b

Posted: Sat Dec 29, 2007 11:00 am
by fordlover35
its just heat.

RE: Coleman furnace model 7656b

Posted: Sun Dec 30, 2007 4:57 am
by Robert
Blower Motor # 7966-311P @ $109.78 + $12.00 shipping .


It can be seen and ordered through PayPal from left side of page here:

http://www.mobilehomerepair.com/ColemanGas.html


Or, by emailing Mark to have him invoice you for it at [email protected]


If outside the U.S., let us know for added info on ordering.



Thanks for inquiring,
Robert

RE: Coleman furnace model 7656b

Posted: Sun Dec 30, 2007 10:53 am
by fordlover35
THANK YOU so very much for all of your help!

RE: Coleman furnace model 7656b

Posted: Sun Dec 30, 2007 7:27 pm
by Robert
Hi,

You're very welcome.


Take care and best wishes,
Robert